EIC for the CU and new circuits, PIR for the existing.if I change a consumer unit and do a part rewire can i put all circuits on eic?I would not be able to confirm routing of existing cables etc. could this be noted down on cert. I have to certify whole installation.
That's a bit harsh, Noz, and also not correct.Sorry, but the above posts are wrong.You only need to issue an EIC, if carefully write what you did in the description of the works carried out box what you did and didn't do then it's covered; also put LIM in the routing of cables box on the inspection schedule.
So, Zeespark, you don't stand corrected, you are, in fact, correct.if I change a consumer unit and do a part rewire can i put all circuits on eic?I would not be able to confirm routing of existing cables etc. could this be noted down on cert. I have to certify whole installation.
Valid point, interpretation is always that stumbling block on forums!. I think we need Tobo to confirm his original point a bit clearer. Re reading the last sentence with an extra word could change the question perhaps; "Do I have to certify whole installation?" or "I do have to certify whole installation". Can we have a bit more detail please Tobo?PC,He's not saying he thinks he is certifying the whole installation - I think he's saying that he has to........as in, it's part of the job he has been asked to do.![]()
In which case he will be issuing a PIR on the existing.
Yes, sorry about that it's just that obviously I read / misread the OP differently to you.That's a bit harsh, Noz,
:Applaud :Applaud:SaluteWhen you carry out a CU change there is no need to issue a PIR. Of course, you can if you want.You do need to issue an EIC to cover the work you have done, namely replacement CU. When changing a CU it is necessary to carry out basic checks to ensure the existing circuits are safe to be reconnected to a new CU. You would fill in the results of these checks on the results schedule. On the inspection schedule, you would normally put "n/a" in the box for safe zones.
If you do other works as well, such as an additional circuit or repairs / alterations to an existing circuit, then on the EIC page 1, in the box entitled "extent of installation covered by this certificate" you would put a description of the works carried out. If these works included new cables in safe zones, then on the inspection schedule you would tick that box. The tick in the box is only applicable to the work you have carried out as described in the "extent of installation...." box. The tick in the box does not certify that existing cables are in the safe zones.
The same principles apply to all the boxes on the inspection schedule - you tick those which are applicable to the work you have carried out.
If by "certify whole installation" you believe you are certifying the existing installation, then you are mistaken. You are not. That's what the "extent..." box is for, so that you can state exactly what it is you are certifying.
If in the course of the work, you find items which do not conform to the regs (eg you can see from the plaster marks there is cabling outside the safe zones) but you have not been commisioned to repair these items (and they are not unsafe), then the EIC has a box entitled "comments on existing installation" where you can note such items.
Does that help?
Thanks, Specs. High praise indeed.if I can issue eic's but not pir's. can I issue a limited eic for all circuits on new cu. new and old. I haven't joined a scheme yet, but am just weighing up all possible outcomes before parting with someone else's cashthanks for all the help.