Hi,
Im going to change my CU indoors for my assessment with Elecsa/NIC and want to ask the following questions.
View attachment 528
If the picture has worked above the earthing conductor from TNS sheath to MET is only about 3" long but uncovered/uninsulated wires. Is this normal and OK?
Also the main protective bonding conductors are 6mm with main earthing conductor being 6mm too. OSG recommends 16mm MEC and 10mm MPBCs so will these have to be upgraded. (Concrete floors/Walls and gas meter and water meter on wall outside maisonette so will be a nightmare to get there)
Also all the wiring is in conduit which is being used as the earth and im trying to find where the conduit is bonded to MET and have found some BS951 clamps but lookn like 4mm cable has been used.
It would have been installed approx 1974 with CU being changed approx 1994 I recon.
View attachment 529
Thats the CU if that helps any?
Thanks for any help you give me
Cheers
Im going to change my CU indoors for my assessment with Elecsa/NIC and want to ask the following questions.
View attachment 528
If the picture has worked above the earthing conductor from TNS sheath to MET is only about 3" long but uncovered/uninsulated wires. Is this normal and OK?
Also the main protective bonding conductors are 6mm with main earthing conductor being 6mm too. OSG recommends 16mm MEC and 10mm MPBCs so will these have to be upgraded. (Concrete floors/Walls and gas meter and water meter on wall outside maisonette so will be a nightmare to get there)
Also all the wiring is in conduit which is being used as the earth and im trying to find where the conduit is bonded to MET and have found some BS951 clamps but lookn like 4mm cable has been used.
It would have been installed approx 1974 with CU being changed approx 1994 I recon.
View attachment 529
Thats the CU if that helps any?
Thanks for any help you give me
Cheers