I am just curious guys,if you change a CU,doesn't all the installation becomes your responsibility ?

 
Hello!

Had same job couple of weeks ago. Metal light fitting in kitchen and bathroom.So I've installed New consumer unit with RCD and earthed that lamps fittings with 1.5mm green yellow wire, sticked label.Done everything as stated on ESC guide.Now can sleep without worries.

Thanks

 
Hello!Had same job couple of weeks ago. Metal light fitting in kitchen and bathroom.So I've installed New consumer unit with RCD and earthed that lamps fittings with 1.5mm green yellow wire, sticked label.Done everything as stated on ESC guide.Now can sleep without worries.

Thanks
Shouldn't a separate run CPC be bigger than 1.5mm...

for compliance with 543.1.1 & 543.3.1 ?

 
Wow, a council actually applying some good practice. Which council is that Robin?Doc H.
I do a lot of sub-contracting for my local housing trust and believe me they show very little common sense and any practice, good or bad, is left in the hands of the sub-contractor. I've removed all sorts of horrors and walked straight back out of some properties due to diy bodging by so called "proper electricians" or tennants.

 
No chance of running seperate CPC then.

I often find no CPC visible, but on checking cable have found cpc just cut away - if enough slack this can often be reinstated

You may already have thought of this, just trying to help

---------- Post Auto-Merged at 13:16 ---------- Previous post was made at 12:56 ----------

No chance of running seperate CPC then.

I often find no CPC visible, but on checking cable have found cpc just cut away - if enough slack this can often be reinstated

You may already have thought of this, just trying to help

 