here's a diagram. if anyone is unable to work out how you can get a shock from the neutral' date=' i suggest you go try it in your own house. just make sure you call an ambulance first.
[img']
http://i22.photobucket.com/albums/b314/andrew2022/borrowedneutral-1.jpg
Oh dear, my comments seem to have upset some.
so let me explain my thought process and understanding of why I gave the advice I did.
The circuit you have shown there is a loop through circuit. Any such loop through circuit that is likely to be of an age to be a candidate for a borrowed neutral would be loop through in the light fitting (loop through at the switch is mostly a more recent configuration)
Now, I FULLY ACCEPT that in the case of a loop through circuit with a borrowed neutral, then unlooping the neutral in the process of changing a light fitting could lead to you receiving a shock.
BUT, and here's the but, the whole point of a loop through circuit is you have a live and it CORRESPONDING neutral at EVERY light fitting. So you would have to be working really really hard and make some really stupid and deliberate mistake to ever manage to get a borrowed neutral on a loop through circuit.
Consequently, I have NEVER encountered a loop through circuit with a borrowed neutral so never ever gave a thought to the fact that it
could happen and could be dangerous.
The ONLY time I have encountered a borrowed neutral is with the old "all back to one junction box" circuit (usually one junction box per floor). Borrowed neutral is common with those to save on the number of cores going from upstairs to downstairs.
So here is the next BUT. With the "all to one junction box" circuit, there is only ONE live and only ONE neutral to each light fitting. So even with a borrowed neutral, and two supplies, changing a light fitting is not dangerous as you will never be splitting the neutral when you remove the fitting. The usual rules apply, the only way you will get a shock is by not isolating the supply to that light fitting and not testing for dead.
The ONLY time you would split the neutral and hence risk a shock with an "all to one junction box" circuit is if you were doing some major work in the big lighting junction box. That I assume is beyond the realms of a DIY light fitting change and would only be done by an electrician who knows what he is doing.
So I still stand by the fact I would be happy personally that two supplies to a borrowed neutral lighting circuit of the "all to one junction box" type does not pose a
significant danger, and operationally is preferable.
I fully accept a borrowed neutral in a loop through circuit DOES poses a significant danger, but re iterate I have never encountered that, and can't imagine how it could occur.
This discussion is about a CU change. The main criteria of a CU change is to ensure the installation is "no less safe" than before. As such we are not required to bring everything up to current standards. We have to make a judgement that the work we do improves safety. Taking all the above into consideration, I still contest that having a borrowed neutral lighting circuit on two MCB's, sharing the same RCD is still a lot safer than it was before. After all that borrowed neutral circuit has been there for probably 30 years or more posing the same risk.
I take my job seriously and always try to do a safe, well thought out job. I have thought out the consequences and possibilities of a borrowed neutral lighting circuit, but came to a different conclusion to others. I don't think that makes me reckless or a bad electrician.
I try to consider each job individually, and like I have already said, if ever I do encounter a loop through lighting circuit with borrowed neutrals that really could pose a real danger I would not put them on separate MCB's. But better still, if it was a loop through, it should be simple to find and correct the borrowed neutral in the first place.
I think what this highlights is that I try to analyse the circuit and make an informed judgement on each individual case as to what is safe and what is not safe. Some prefer to read a regulation and apply a blanket ruling, without actually considering if there is any real danger or not in a particular situation. That does not make one person right and the other wrong, it just highlights a different approach (I come from an industrial background so am perhaps a little more used to "problem solving" than some might be)
The important thing is we are discussing possible scenarios and it may highlight dangers some had not anticipated, or may show that some perceived dangers are not real. But if it gets us all
thinking and
analysing what we are doing, then that has to be for the better.