+1 with Andy, contact Dno
Ive spoke to dno in past, they are only responsible upto the service head, the meter tails and meter are the responsibility of the supplier, arguably the tails between the meter and cu are the consumers responibility.
The 3 meters is the length at which the dno will g/tee protection of the cable.
Now the way i see it is from the service head the installation needs to meet BS7671, now if you Ze is quite low for the type of fuse then i see no issue with longer tails providing BS7671 is met. The suppliers may require an isolator and it would be good practice to do so anyway.
If you ZE is not so low and little room for error then a switched fuse will be required to protect the remainder of the tails/ distribution circuit.