There are 4 issues here.
1. RCD may not trip as inverter output is not true pure sine wave.
2. Inverter will continue back feeding other circuits on the RCD after it has tripped for up to 5 seconds.
3. The inverter is a generator. It is earthed, it has to be. Now, is there an N-E link at the inverter as would be expected at a normal generator. If so then, there is a danger. The earth is continuous from the inverter frame to true earth, it has to be. Whilst the N of the DNO supply is disconnected, the inverter N is still connected to the fault side of the RCD. Remember, this is a generator, not a consumer, so an internal N-E link is NOT prohibited. Is this why most inverters are not allowed on TT?... Remember, this link could switch on loss of synchronisation feed, so would not be seen by an RCD protecting the DNO supply as it would not be in place until the DNO feed was off.
4. IT systems are not allowed in consumer installs in the UK.
The issue is that there is not enough information on the internal configuration of the inverters for us to make a definitive judgement, we can do all the tests and make all the measurements we like, but, this will simply be empirical data. The definite specification of the inverter will give the actual danger, and no one is telling.
So, we have to err on the side of caution IMHO.
1. RCD may not trip as inverter output is not true pure sine wave.
2. Inverter will continue back feeding other circuits on the RCD after it has tripped for up to 5 seconds.
3. The inverter is a generator. It is earthed, it has to be. Now, is there an N-E link at the inverter as would be expected at a normal generator. If so then, there is a danger. The earth is continuous from the inverter frame to true earth, it has to be. Whilst the N of the DNO supply is disconnected, the inverter N is still connected to the fault side of the RCD. Remember, this is a generator, not a consumer, so an internal N-E link is NOT prohibited. Is this why most inverters are not allowed on TT?... Remember, this link could switch on loss of synchronisation feed, so would not be seen by an RCD protecting the DNO supply as it would not be in place until the DNO feed was off.
4. IT systems are not allowed in consumer installs in the UK.
The issue is that there is not enough information on the internal configuration of the inverters for us to make a definitive judgement, we can do all the tests and make all the measurements we like, but, this will simply be empirical data. The definite specification of the inverter will give the actual danger, and no one is telling.
So, we have to err on the side of caution IMHO.