This isn't possible. You can't work back from an annual energy consumption figure to a run current. Even if you assume it's plugged in 24/7 you don't know the running time because of the thermostatic control; you can't go from kWh to kW without knowing the exact hours. The smallest generally available refrigeration compressor is 1/12hp. Looking at the easiest three makes to find on the internet the Embraco is 72watts, the Techumseh is 76w and the electrolux(ACC) is 70watts. Obviously if the compressor runs 25% of the time because of the thermostat then you get the 0.4kWh per day you mentioned above but your run current will be 0.3Amps and not the 0.073A you calculated.
I would say the only certain methods of finding the run current is either by accurate measurement or the info plate on the appliance or in the manual.
However....
When designing circuits we take into account diversity...
Not just the peak load for a small percentage of the time...
On average over the course of a 24hr period the current drawn by a single fridge will be as per my rough back calculations ...
Just as when we design for a ring or radial circuit, we do not assume ALL appliances are going to be running full load current 24/7..
Or lighting circuits we do not assume all lights are on together...
The total load averages out over the 24hr period..
even though as we all know circuits can quite happily take higher currents than both the cable and protective device are rated at for short periods...
The question was about 3x under counter fridges, I doubt 3x fridges will all be drawing the max full load simultaneously for the bulk of the 24hour period.. It will be averaged out..
Same principle as how many houses cope quite easily with 60A main fuse & 16mm2 tails..
when the apparent max load could appear to be 100A+ if you just look at all the circuit breakers and all of the appliances and loads connected...
Diversity.. Pg 109 onward OSG
or
pg 81 & 177 onward GN1
By your own calcs the compressor may only be running 25% of the time..
so 3x fridges probably only 75% between them..
so 25% of the day the cable is carrying naff all !..
With something like domestic under counter fridges..
I can't see you will be to far off calculating an average (over 24hrs) for a single item and multiplying by 3 fridges....
What are you going to do if you do know the exact max load running current?
add em all together as if they are all running full load 100% 24/7 ??
:C