Hi guys
this install is overhead supply, TT with an voltage operated leakage breaker, the rod looks to be an old copper pipe and ra is around 600 ohms.
new cu fitted but i am struggling to get a rod in as there is a lot of concreate and i cant get one in a suitable place with a decent reading. this is the cut out, the cable is the gas water bonding done by a while back by a plumber.
as its over head, TT, and no pme lables am i right in thinking the dno will have to come out to see if it is pme?
thanks