Hi,
As you most probably know Im changing my dads board for Elecsa Assessment and Ive been round there today to do the dead tests and the results are as follows. The old board is a BS3036 rewirable (pictures attached) and it has been wired up from 1970 onwards so theres a mixture of cables in there. Some are solid core and some are stranded and testing was grief as the stranded cables earths (cpc's) have all been twisted together so had to untwist them all to do the continuity tests.
Gas Bonding - 0.00 ohms (very short run 10mm)
Water Bond - 0.02 ohms (10mm)
Kitchen Ring
L-L - 0.35 ohms
N-N - 0.35 ohms
E-E - 0.89 ohms (this is very high but could not find loose connection anywhere*)
L-N Crossed
Socket 1 - 0.17 ohms
Socket 2 - 0.17 ohms
Socket 3 - 0.17 ohms
Socket 4 - 0.18 ohms
Socket 5 - 0.16 ohms
L-E Crossed
Socket 1 - 0.28 ohms
Socket 2 - 0.30 ohms
Socket 3 - 0.30 ohms
Socket 4 - 0.39 ohms
Socket 5 - 0.31 ohms
I understand these should be within 0.05? of eachother so are these ok other than socket 4 being a bit high (maybe loose connection?*)
When I had the legs hanging out of the board disconnected just before I was about to do IR test, the probes were connected to Line & Neutral and the meter was on continuity and I saw it reading continuity of 14.3 ohms. I did make sure I unplugged everything in sight but the washing machine & dishwasher must still have been plugged in as I couldnt get to these to unplug them, would this 14.3 ohms be them?
Also one last question on this post (as Ive got loads to ask but dont want to do a massive post as some questions may get missed) As i was reading continuity between Line & Neutral I didnt want to send 500V DC and blow something up (central heating has been wired up from ring too I believe with no FCU to isolate) so I IR tested 250V DC L&NtoE and I got a reading of 55.6MOhms which is a pass as above 1MOhm but the meter was creeping whilst doing this test. It was rising and rising?
Ill finish babbling now as Ive got loads of other questions so will start a new post.
Thanks in advance for any pointers/advice and maybe this post may help newbies as well.
Cheers
Matt
Where ive put * can you give me any guidance as to if this is ok or needs further investigation
ThanksGuinnessrayGuinness
As you most probably know Im changing my dads board for Elecsa Assessment and Ive been round there today to do the dead tests and the results are as follows. The old board is a BS3036 rewirable (pictures attached) and it has been wired up from 1970 onwards so theres a mixture of cables in there. Some are solid core and some are stranded and testing was grief as the stranded cables earths (cpc's) have all been twisted together so had to untwist them all to do the continuity tests.
Gas Bonding - 0.00 ohms (very short run 10mm)
Water Bond - 0.02 ohms (10mm)
Kitchen Ring
L-L - 0.35 ohms
N-N - 0.35 ohms
E-E - 0.89 ohms (this is very high but could not find loose connection anywhere*)
L-N Crossed
Socket 1 - 0.17 ohms
Socket 2 - 0.17 ohms
Socket 3 - 0.17 ohms
Socket 4 - 0.18 ohms
Socket 5 - 0.16 ohms
L-E Crossed
Socket 1 - 0.28 ohms
Socket 2 - 0.30 ohms
Socket 3 - 0.30 ohms
Socket 4 - 0.39 ohms
Socket 5 - 0.31 ohms
I understand these should be within 0.05? of eachother so are these ok other than socket 4 being a bit high (maybe loose connection?*)
When I had the legs hanging out of the board disconnected just before I was about to do IR test, the probes were connected to Line & Neutral and the meter was on continuity and I saw it reading continuity of 14.3 ohms. I did make sure I unplugged everything in sight but the washing machine & dishwasher must still have been plugged in as I couldnt get to these to unplug them, would this 14.3 ohms be them?
Also one last question on this post (as Ive got loads to ask but dont want to do a massive post as some questions may get missed) As i was reading continuity between Line & Neutral I didnt want to send 500V DC and blow something up (central heating has been wired up from ring too I believe with no FCU to isolate) so I IR tested 250V DC L&NtoE and I got a reading of 55.6MOhms which is a pass as above 1MOhm but the meter was creeping whilst doing this test. It was rising and rising?
Ill finish babbling now as Ive got loads of other questions so will start a new post.
Thanks in advance for any pointers/advice and maybe this post may help newbies as well.
Cheers
Matt
Where ive put * can you give me any guidance as to if this is ok or needs further investigation
ThanksGuinnessrayGuinness