IMO a radial circuit suppling socket should be on a 16A minimum with the 2.5mm cable.
The only 1.5mm cable I would be happy to use for this application is MICC.
Having said that all suggestions mentioned are not incorrect but IMO the circuit design is very poor.
6A protection for such a circuit COME ON.
So electrical craft principles means nothing to you, which we were all taught at college?.
Its not all about BS7671 its about standard working practices.
It has nothing to do with my standards or option, its how I've been taught out in the field and technical
college. Your answer is very confusing you say you would not do it so you must also have an issue designing such a circuit. Why are you throwing in EICR? With 46 years experience in the industry I can honestly say I'm more than competent in that area.
Possibly your craft principles were different to many other industry recognised standards? (also taught going back over many many years?)
e.g. basic design where you have a known load, was to select an overcurrent protective device sufficient to supply the load, and an appropriate cable type and size suitable for the rating of the protective device, allowing for derating correction factors, installation methods and volt-drop... etc..
Then after that comes the business economics element where there is no point over-engineering a solution that is more expensive when a cheaper solution can meet all of the electrical and safety elements of the design.
Hence why back in the days of the old regional electricity boards.. (I am in the midlands and ours was the "MEB")...
When their engineers came and installed economy7 night storage heaters, you often got a 3kW storage heater, off a 13A FCU, (or 20A DP switch), fed by a 1.5mm T&E connected to a 15A 3036 wire fuse in the old Wylex fusebox!
Which is no worse than had it been single 13A socket.... ?
However back to the OPs actual question..
He wants a socket to plug in a "CAMERA" (guessing its a plug-in transformer jobbie)..
It is NOT a socket for general purpose... No kettles/toasters/tumble driers etc..
I am struggling to understand why you would consider it is required to have a 2.5mm 16A supply for a Camera PSU that could probably run off a USB socket from a laptop??