Digital Spot Welder ..
Danny
Apr 1, 2009
91
Chaps .. does anyone have any experience of setting up a circuit for one of these .. ?
The manufacturers spec is a 25A supply but I'm reading that they cause significant inrush current so would a C breaker be better from the outset ?
I'd prob go for a type D if you can get one they are a bit more expensive but it does eleviate the start up current.
We used to have them on some machines at the last place i worked at.
Thanks for that ... found a 32A Contactum D type at TLC for a fiver so that's that one sorted ... cheers ..
As long as your fault loop is ok
Looking fine with the sums ... Calculated Zs is 0.11 and 80% of max Zs is 0.29 so hopefully all should be ok ..
Any thoughts on RCD protection ? I'm reading there is quite some leakage from these ... the cable run is 2m ... dedicated circuit for fixed equipment ..