A quick heads up to anyone. Don't use Contactum 2 pole RCBO's for Solar PV
This came from another thread of mine where I needed a mini CU for a shower but there was only a tiny space, so we came up with just a 2 pole RCBO in a slim 2 module enclosure.
I chose a Contactum 2 pole RCBO, and fed the power into the bottom (no manufacturers instructions to say which should be the feed) and the thing self destructed in a puff of smoke on the first press of the test button.
So you CAN'T feed power in to the bottom of a Contactum 2 pole RCBO.
So IF you were thinking of doing anything similar to make a compact mini CU to connect a Solar PV system, you MUST ensure your chosen RCBO can accept power input to either end.
Had you used a Contactum RCBO, even with the supply in the correct end, in the event of the RCD tripping while the solar PV was generating, the "run on" time of the inverter before it shuts down, feeding into the RCBO's output terminals, would likely destroy the Contactum RCBO.
This came from another thread of mine where I needed a mini CU for a shower but there was only a tiny space, so we came up with just a 2 pole RCBO in a slim 2 module enclosure.
I chose a Contactum 2 pole RCBO, and fed the power into the bottom (no manufacturers instructions to say which should be the feed) and the thing self destructed in a puff of smoke on the first press of the test button.
So you CAN'T feed power in to the bottom of a Contactum 2 pole RCBO.
So IF you were thinking of doing anything similar to make a compact mini CU to connect a Solar PV system, you MUST ensure your chosen RCBO can accept power input to either end.
Had you used a Contactum RCBO, even with the supply in the correct end, in the event of the RCD tripping while the solar PV was generating, the "run on" time of the inverter before it shuts down, feeding into the RCBO's output terminals, would likely destroy the Contactum RCBO.