Hi
Just been called out to a Dyson tripping the RCD at a house. Dyson has just been brought back from the manufacturers with a clean bill of health. Board is a Memera 2000 split load with RCD covering house sockets and central heating. Have done a ramp test on the RCD with everything working normally and it trips at 23mA so not too bad. Socket circuit 1 ramp test 25mA. Socket circuit 2 ramp test 23mA. RCD test shows normal tripping times and passes. Property is 10 yrs old and electrically untouched in that time with no external sockets. Have swapped out the RCD and no difference. Vac seems only to trip if both circuits are turned on. No other appliances cause an issue.Have brought the vac back to mine and its not tripping here. Any ideas?
Just been called out to a Dyson tripping the RCD at a house. Dyson has just been brought back from the manufacturers with a clean bill of health. Board is a Memera 2000 split load with RCD covering house sockets and central heating. Have done a ramp test on the RCD with everything working normally and it trips at 23mA so not too bad. Socket circuit 1 ramp test 25mA. Socket circuit 2 ramp test 23mA. RCD test shows normal tripping times and passes. Property is 10 yrs old and electrically untouched in that time with no external sockets. Have swapped out the RCD and no difference. Vac seems only to trip if both circuits are turned on. No other appliances cause an issue.Have brought the vac back to mine and its not tripping here. Any ideas?