soil (/earth/concrete etc) is a conductor. not an insulator. obviously not as good at conducting as copper. which is why you get high readings (compared to TN)thanks.Thats what I thought, but I find it hard to grasp he idea that the fault current could travel through the ground back to the transformer.
I put my first rod in the other day and got a good reading of about 24 ohms. So that distance to the transformer, which I guess could be 100's of meters away only has a resistance of a few ohms, but a millimeter of PVC has a resistance of millions of ohms. Makes my mind boggle.
Does the fault current not get confused by other metallic things under ground
184ohms Is below the 220ohms so is ok. A lot depends on what ground is made off. If you are getting zs of 74.4ohms that is probably through one of the service pipes. I would be suprised if you could bring it down much more with another rod.do you measure the ze the same way on a TT, use the earth cable attached to the rod?ive got a reading of 184omhs for ze and 74.4ohms for zs on socket circuit.
all rcd protected and bonding to gas and water fine.
have suggested to install an xtra rod to try and bring reading down, have i done right?
cheers wayne
I thought that it was 200 ohms and the 100 ohms was one of nic's special rules. Or is this another myth lolBS7671 suggests that anything over 100ohms could be unstable.
Depends which standard your working to, spin probably meant BS 7430 which states 100 ohmsI thought that it was 200 and the 100 was one of nic's special rules. Or is this another myth lol
7671 does say 200. NIC says 100, but then NIC dont make the rulesI thought that it was 200 ohms and the 100 ohms was one of nic's special rules. Or is this another myth lol