Hi again,

So back at the bank again today and I have another question for you all. Recently bought myself a Earth leakage clamp meter and decided to try it out today, imagine my shock and horror as I clamp the tails of one DB and find 4.2A of leakage apparently. So I switch off the board and it drops to 12mA. I then switch it back on and back to 4A it goes and when I switch off the other DB it drops down again. So when both boards are on it’s at 4A but when either board is off, individual DB’s are between 10-12mA….does that make sense and if yes can anyone explain why?
 

Geoff1946

Well-known member
Joined
Dec 8, 2016
Messages
1,654
Reaction score
235
Location
Blackpool
Just switch on both boards, watch the 4amp, "unbalance" on your meter, and then switch off each MCB in turn. When the mystery current disappears that's the offending circuit with mis-wired neutral. Must be something fairly significant; it's about 1 kW.

Afterthought; It could be more than one.
 
Last edited:

Sidewinder

The Snake™
Staff member
Administrator
TEF Moderator
Supporting Member
Joined
May 6, 2010
Messages
15,279
Reaction score
308
Location
UK
Current which has its origins outside the installation, typically from N or E and then manifested in the installation.
 