There are options, however, for me and not posessing a leakage clamp, I would go for L&N any reading you then get would be the leakage.
The Delta of the phase & N currents.
Why?
I would do this because it is not necessary for leakage to "leave" the installation through the earth conductor, it could take parallel paths.
Water pipe, gas pipe, structural steel, oil etc.
HTH