Hi folks.
First post, but need some pointers.
Trying to complete a test on an empty property (to return to Housing Associatin)
1. Measured incoming Voltage at CU was 194V. Unable to complete loop/Zs/RCD tests (no probs I thought ..meter, kewtech kt64, not playing cause the supply V is too low.
2. Distribution company checked it out and reported incoming V of 237V.
3. Revisited today. V at main switch = 222V.
However open switch and it goes up to 230V+
4. And....Meter indicates earth is present, but when trying to measure Ze with main switch open I'm getting >1999 ohms.
With switch closed I'm getting "N - PE Hi V" (E-N fault?)...this still doesn't explain the >1999.
Am I missing something simple or could there be a suppliers meter fault
Thanks in advance