hi folks,i've been asked by a customer to provide earthing equipment for a swimming pool. He doesn't seem to know exactly what is needed but has been told to get down to 20 resistance and that he may have to use a copper
earthing plate.Has any one had any experience with this type of install? He is
an NICEIC spark by the way not a d.i.y-er
thanks, Barry
there is a ref in the big red book 702.410.3.4.3. For connection to the main equipotential bonding?
Guiness Drink
Right...
1/ I have NO personal experience of installing swimming pool installations...
But I do have customers with swimming pools.
2/ Is this pool Indoor OR Outdoor?
e.g. I have a customer with an outdoor garden pool which has a small building with pump & filter equipment...
because this is Remote to the main house it has its own rod 'TT' instalkltion...
dunno what the resistance is though?!!!
3/ That quote of Sarni in '702.410.3.4.3' (ii), page 171 of big red...
is in relation to TN-C-S installation, it suggests an earth mat OR electrode with Earth loop less than 20ohm is connected to protective equipotential bonding.
I am guessing that this job is a TN-C-S (PME) and the guy needs to get a local earth (mat OR rod) by the pool with 20ohm or less.
My first question would be.....
What IS the resistance if you just stick in a standard Rod??
once you know what that is... you can then decide the best course of action....
e.g. if Ze of rod is 25 - 40 ohm..
I would probably go down the "try a second rod option" first.
I am assuming that if it is a PME installation .. the pool is considered as another exposed conductive part likely to introduce an earth notational,
So try rods, tapes, etc to get supply equipment as low as possibly.
:|