I don't see what the problem is here? You issue an EIC for the work that you do, namely the new tails, which is listed in the "Extent" box. There is nothing to stop you using the same certificate to record the results of your prior inspection.
We had a discussion similar to this (CU change, actually) back last October but I don't know how to link to old posts so I have copied my reply and pasted below.
"I produce my own EIC's, modeled around the standard form, and below the "Notes and Guidance for Recipients" box, I have a "Further Information" box.
The first paragraph of my further information contains the following permanent entry:-
"If the work undertaken is a replacement consumer unit only, then the circuit information supplied on the Schedule of Inspections and the Schedule of Test Results may be incomplete and only reflects the inspections and tests undertaken for the purpose of verifying that the various circuits were safe to reconnect. It does not indicate that the electrician / inspector has altered or added to those circuits, nor does it make the electrician / inspector responsible for any subsequent faults discovered on those circuits.
Whether or not this covers my a**e satisfactorily will only ever be determined in a court of law if a situation ever arises. My scheme assessor seems to approve, though.
Please feel free to copy this verbatim if you feel it may be useful to you. "
In your case, it's not a CU change but a change and connect of tails. The principle is still the same.
We had a discussion similar to this (CU change, actually) back last October but I don't know how to link to old posts so I have copied my reply and pasted below.
"I produce my own EIC's, modeled around the standard form, and below the "Notes and Guidance for Recipients" box, I have a "Further Information" box.
The first paragraph of my further information contains the following permanent entry:-
"If the work undertaken is a replacement consumer unit only, then the circuit information supplied on the Schedule of Inspections and the Schedule of Test Results may be incomplete and only reflects the inspections and tests undertaken for the purpose of verifying that the various circuits were safe to reconnect. It does not indicate that the electrician / inspector has altered or added to those circuits, nor does it make the electrician / inspector responsible for any subsequent faults discovered on those circuits.
Whether or not this covers my a**e satisfactorily will only ever be determined in a court of law if a situation ever arises. My scheme assessor seems to approve, though.
Please feel free to copy this verbatim if you feel it may be useful to you. "
In your case, it's not a CU change but a change and connect of tails. The principle is still the same.