Hi all
done my 2391 a few years ago but never got a chance to use it properly as my old firm had 2 full time testers, so obviously a bit rusty. i need help on a couple of entries on the NICEIC electrical installation cert ICN2
the work i'm doing is adding some lighting and power to an existing DB on the 8th floor and the DB is connected to a rising busbar, i have no access to the main incoming supply so how do i find out
page 2 nature of supply parameters:the Earthing arrangement, the PFC, external earth fault loop impedence Ze, and also the characteristics of primary supply overcurrent protective devices.
page 5 :characteristics at this distribution board
The DB is mechanically fixed via trunking to the tap off unit and has a 25mm earth cable from the busbar casing to the db so how do i get the Zs without disconnecting all the out going earths from the board (including existing circuits already in the board)
and finally as the board is 3 phase but all outgoing supplies are single phase do i do the pfc as the highest of the 3 phases or do the rule of thumb and double the reading
lastly i have fitted some merlin gerin rcbo's and they still trip when i do loop test on the circuits even though the robin tester has D lock, can i substitute the rcbo for a mcb, get the readings ,then put the rcbo back
thanks:C
done my 2391 a few years ago but never got a chance to use it properly as my old firm had 2 full time testers, so obviously a bit rusty. i need help on a couple of entries on the NICEIC electrical installation cert ICN2
the work i'm doing is adding some lighting and power to an existing DB on the 8th floor and the DB is connected to a rising busbar, i have no access to the main incoming supply so how do i find out
page 2 nature of supply parameters:the Earthing arrangement, the PFC, external earth fault loop impedence Ze, and also the characteristics of primary supply overcurrent protective devices.
page 5 :characteristics at this distribution board
The DB is mechanically fixed via trunking to the tap off unit and has a 25mm earth cable from the busbar casing to the db so how do i get the Zs without disconnecting all the out going earths from the board (including existing circuits already in the board)
and finally as the board is 3 phase but all outgoing supplies are single phase do i do the pfc as the highest of the 3 phases or do the rule of thumb and double the reading
lastly i have fitted some merlin gerin rcbo's and they still trip when i do loop test on the circuits even though the robin tester has D lock, can i substitute the rcbo for a mcb, get the readings ,then put the rcbo back
thanks:C