Hi,
I recently requested a report on my domestic Installation. Some of the wiring dates back to the late '60's when the house was built. The assessment has been marked as Satisfactory but on reading further I was surprised to learn that an insulation test wasn't carried out for the following reasons "Property is occupied and items vulnerable to testing" I also note that the testing equipment used for Earth Fault Impedence, Continuity & Insulation Resistance has not been specified although there is a serial number in the MFT panel. I would have thought insulation resistance would be extremely important given the age of the wiring. Am I being paranoid?
I recently requested a report on my domestic Installation. Some of the wiring dates back to the late '60's when the house was built. The assessment has been marked as Satisfactory but on reading further I was surprised to learn that an insulation test wasn't carried out for the following reasons "Property is occupied and items vulnerable to testing" I also note that the testing equipment used for Earth Fault Impedence, Continuity & Insulation Resistance has not been specified although there is a serial number in the MFT panel. I would have thought insulation resistance would be extremely important given the age of the wiring. Am I being paranoid?