Had an interesting problem last year which I invite comments on.
The main supply upgraded at one of my regular customers,Printers, to 200amps.
I installed 4 x 70mm meter tails from main switch to the networks metering. Thinking I'd be clever I seperated them on the tray by their own diameter as recommended.
Problem: The other side of the wall (10" solid block) to the meter cupboard is an office using computers, the monitors having interference lines on the screens until we moved them two metres away. Same to the right of the cupboard on another screen.
I screened the screen with an earthed piece of sheet steel to no avail.
In the end we got an elect. consultant on site who recommended the 70mm tails were reclipped in trefoil , result, bringing them together caused each phase to cancel out the eddy currents of the next and no interference to screens . An electromagnetic field extending about 5 ft from the cables and through a solid block wall. Mmmmm !
The main supply upgraded at one of my regular customers,Printers, to 200amps.
I installed 4 x 70mm meter tails from main switch to the networks metering. Thinking I'd be clever I seperated them on the tray by their own diameter as recommended.
Problem: The other side of the wall (10" solid block) to the meter cupboard is an office using computers, the monitors having interference lines on the screens until we moved them two metres away. Same to the right of the cupboard on another screen.
I screened the screen with an earthed piece of sheet steel to no avail.
In the end we got an elect. consultant on site who recommended the 70mm tails were reclipped in trefoil , result, bringing them together caused each phase to cancel out the eddy currents of the next and no interference to screens . An electromagnetic field extending about 5 ft from the cables and through a solid block wall. Mmmmm !