Scott:
I know what our Albert is getting at.....
In order to measure the Ze, you have to physically disconnect the earthing conductor - yes?
especially with their being no bonding; you`d have intentionally removed the ONLY source of protective earthing for testing purposes, whilst part of the installation was powered up? Baaaaaaaaad idea, AFAIAC mate - and if there is a server being fed from this supply; its likely to be a switched-mode unit; which has inherent leakage anyway!!!!!
IF there is NO structural steel, and NO bonding, then a Zs reading shouldn`t be too far away from a Ze anyway? If you`re still worried; the customer declining a full shutdown automatically gives rise to a "lim" on Ze by measurement anyway......
Yes?
I know what our Albert is getting at.....
In order to measure the Ze, you have to physically disconnect the earthing conductor - yes?
especially with their being no bonding; you`d have intentionally removed the ONLY source of protective earthing for testing purposes, whilst part of the installation was powered up? Baaaaaaaaad idea, AFAIAC mate - and if there is a server being fed from this supply; its likely to be a switched-mode unit; which has inherent leakage anyway!!!!!