Just need to check this with you guys and if needed I can go back to correct.
Situation I have installed some more supplies for single phase LG air con units, my wholesaler sold me 32amp Europa 3 pole isolators which have seperate terminal blocks labelled Neutral and earth in addition to the 3p switch.
Now I terminated Line conductor in L1 and was going to put the Neutral in L2 so as to provide double pole isolation, however changed my mind and used the terminal block for the Neutral conductor as I thought it didnt seem right to put a Neutral in a L2 termination and I didnt have my labelling machine with me.
Have checked regs book 537.2.1.1 and it seems that I am ok as supplies at both properties are TNS and TNCS and so Neutral is reliably conected to earth and therefore no need to isolate.
If I have cxcked up then can easily go back as both places are local.
Situation I have installed some more supplies for single phase LG air con units, my wholesaler sold me 32amp Europa 3 pole isolators which have seperate terminal blocks labelled Neutral and earth in addition to the 3p switch.
Now I terminated Line conductor in L1 and was going to put the Neutral in L2 so as to provide double pole isolation, however changed my mind and used the terminal block for the Neutral conductor as I thought it didnt seem right to put a Neutral in a L2 termination and I didnt have my labelling machine with me.
Have checked regs book 537.2.1.1 and it seems that I am ok as supplies at both properties are TNS and TNCS and so Neutral is reliably conected to earth and therefore no need to isolate.
If I have cxcked up then can easily go back as both places are local.