Hi all,
Our company recently tested a local factory and I have a couple of questions relating to some of the results obtained.........
The sub station is in the factories car park so we have an extremely low Ze (checked with 3 different meters, all say <0.01 ohms. As a result of this the PSCC/PFC is rather high to say the least (>19.9KA at incomer). The majority of the Distribution Boards are the old MEM M9 type (9KA) but all of the sub main cables are protected by BS88-2 Fuses (80KA). Is it ok to rely on the BS88 fuses to cover the excessive PSCC/PFC readings obtained at the Distribution Boards?
Secondly (hope it`s ok to post two things in one here?), while inspecting the Distribution Boards we discovered that nearly all of the supply Neutrals are far smaller than the phase conductors. The occupants of the factory are not the people the building was originally designed for and there is quite a lot of equipment now requiring Neutral connections (am thinking that originally the Neutral would have been just for local lighting and small power).
Would you agree that we should advise the customer to increase the size of the Neutrals to that of the Phase conductors? (In some cases the Phase conductors are 120mm with a 16mm Neutral conductor).
Many thanks
Colport
Our company recently tested a local factory and I have a couple of questions relating to some of the results obtained.........
The sub station is in the factories car park so we have an extremely low Ze (checked with 3 different meters, all say <0.01 ohms. As a result of this the PSCC/PFC is rather high to say the least (>19.9KA at incomer). The majority of the Distribution Boards are the old MEM M9 type (9KA) but all of the sub main cables are protected by BS88-2 Fuses (80KA). Is it ok to rely on the BS88 fuses to cover the excessive PSCC/PFC readings obtained at the Distribution Boards?
Secondly (hope it`s ok to post two things in one here?), while inspecting the Distribution Boards we discovered that nearly all of the supply Neutrals are far smaller than the phase conductors. The occupants of the factory are not the people the building was originally designed for and there is quite a lot of equipment now requiring Neutral connections (am thinking that originally the Neutral would have been just for local lighting and small power).
Would you agree that we should advise the customer to increase the size of the Neutrals to that of the Phase conductors? (In some cases the Phase conductors are 120mm with a 16mm Neutral conductor).
Many thanks
Colport