Where?There is an allowance in the regs for exporting earths be they TT or TNCS.
Strictly is it possible to export TT? You could rod either end.
Where?There is an allowance in the regs for exporting earths be they TT or TNCS.
What reg would that be, then??And a missing rod connection is safe? There is an allowance in the regs for exporting earths be they TT or TNCS.
COOL. Does that mean EVERYTHING is at phase voltage? Yes?I understand what you are saying about this situation and TT and agree. However I am transporting the earth to domestic outbuildings, garages and the like, as I have seen too many rods not connected, for various reasons. If the earth is disconnected on PME systems nowt works as the neutral has also gone.
Not necessarily, with main bonding acting as a neutral via your garden and your neighbours back up their bonding and to neutral albeit with a slightly higher resistance. Besides, with no neutral, all your earths will be at 230V .If the earth is disconnected on PME systems nowt works as the neutral has also gone.
Yes you are correct.And a missing rod connection is safe? There is an allowance in the regs for exporting earths be they TT or TNCS.
Lots of people used to have outside toilets.sorry i cant read all the threds they are too quick so i may be repeting here.i rang central networks they said export pme is fine just dont mess with there cut out, not totaly convinced with girle on phone so spoke to there enginer in the street he said its ok then i said about droping netrals on there end and he said loads of places have exported and thats how it was when he was a spark
Sorry, just catching up. I do work on loads of farms, I can't think of one which DOESN'T have a pme supply - almost always overhead (I've seen other threads claiming that overhead pme is a no-no). I can think of loads with exported pme earths. Curiously none of them was littered with dead cows / sheep / farmers / vets / electricians.They should never have supplied a farm with PME in the first place........................
i think the point he was makeing was that if they did drop a nutral then loads of people would be at risk, if there is any riskLots of people used to have outside toilets.Lighting circuits used to have no cpc - my gran had an iron that connected to a bayonet lampholder.
Do we thing things are ok because that's how they were done in the past?
Threads never get nasty on here!dont blame u. i have read some previos threads on this export pme they can get nasty