Hi.

I'd like to put in an extra light fitting upstairs.

There are currently 13 light fittings on the circuit - 2 of them with extractor fans wired in.  All the bulbs are CFL, so even with the extractor fans (60W apiece) included, total wattage is less than 250W.

I've read that a standard lighting circuit can support up to 11 light fittings, each of 100W, so does this mean I've loads of headroom for an extension?

Thanks for your time.

 
Is there such a thing as a "standard" lighting circuit?

What do you understand by that terminology?

I think some more information on circuit breakers/fuses

and ratings would assist, as well as conductor sizes.

 
Short answer:-  Most likely YES

Longer answer:-

Basic bit of maths...

Power = Current x Voltage...

the nominal voltage is 230v

the current would be your fuse rating...

probably either 5A or 6A or 10A......

so if 5A power = 1150Watts

so if 6A power = 1380Watts

so if 10A power = 2300Watts

so if you take off your existing 250w...

you have probably got somewhere between 900w and 2050w spare to work with....

*** IF EVERYTHING IS ON SIMULTANEOUSLY ***

However

Lighting circuits normally allow for the fact that not every light is on at the same time

A thing called Diversity...

It is NOT an exact science but one rule of thumb is 66% of total wattage of the connected load...