Went to look at a job this morning. Client wants sockets & lighting to Summerhouse (glorified shed!) which is approx. 18m from CU. Nothing out of the ordinary will be used - power tools, lawnmower etc.
Have read a few previous threads and opinions differ. I've done some calcs and have come up with the following:
Fit 20A RCBO at dwelling CU
Fit 4-way CU in shed with 16A mcb for sockets and 6A mcb for lighting.
Use 4mm 3-core SWA
Chose 4-way CU as client may possibly want a supply to another shed going further down the garden.
I'm sure the setup is TN-S - photos taken will enable someone to confirm this I hope Pray. I'm not sure if I still need RCD protection at the shed CU or a main switch Blushing. I didn't think so as I was covered with the RCBO in the dwelling. Can someone confirm this theory.
I took some pics of CU and will post when I find cable to link my cell to the pc! The CU is located in a cupboard within the kitchen, in the most awkward position you can imagine! For me to access it comfortably, the cooker will have to be removed and the side panel of a unit
I know 17th isn't retro but can the CU remain in this position? To me, it just seems ridiculous to have to practically lie down to get your arm in there :_| I informed the client that I would make enquiries as to whether or not it would need re-locating. Not sure she'll go ahead with job if it does need moving as it will cost too much.
Thanks for any replies.
Nat
One other thing...Elecsa told me that the meter seal can not be broken without the distributor knowing. Is this just a simple case of a call to notify them of work being carried out?
Have read a few previous threads and opinions differ. I've done some calcs and have come up with the following:
Fit 20A RCBO at dwelling CU
Fit 4-way CU in shed with 16A mcb for sockets and 6A mcb for lighting.
Use 4mm 3-core SWA
Chose 4-way CU as client may possibly want a supply to another shed going further down the garden.
I'm sure the setup is TN-S - photos taken will enable someone to confirm this I hope Pray. I'm not sure if I still need RCD protection at the shed CU or a main switch Blushing. I didn't think so as I was covered with the RCBO in the dwelling. Can someone confirm this theory.
I took some pics of CU and will post when I find cable to link my cell to the pc! The CU is located in a cupboard within the kitchen, in the most awkward position you can imagine! For me to access it comfortably, the cooker will have to be removed and the side panel of a unit
I know 17th isn't retro but can the CU remain in this position? To me, it just seems ridiculous to have to practically lie down to get your arm in there :_| I informed the client that I would make enquiries as to whether or not it would need re-locating. Not sure she'll go ahead with job if it does need moving as it will cost too much.
Thanks for any replies.
Nat
One other thing...Elecsa told me that the meter seal can not be broken without the distributor knowing. Is this just a simple case of a call to notify them of work being carried out?