extract fan fire sea

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Andy™

©Resident Geordie™
Supporting Member
Joined
Jan 1, 2009
Messages
30,737
Reaction score
1,451
Location
S. Tyneside
need to put a 4" (possibly 6") duct through a wall for an extractor fan, but its into a different fire compartment. whats the best options? most ive ever needed to do is seal around cables but seems a bit pointless sealing around the duct... so whats the best options?

 
Sounds like you need to install a fire damper that would operate when the fire alarm is triggered. 

 
found these, they look suitable? anyone used them?

PYROCHECK-image_1.jpg


http://www.vent-axia.com/product/pyrocheck-intumescent-fire-dampers-round-150mm.html

 
I've done some 12" duct in a BFO multinational,  steel duct that was joined at the fire compartment separation with a special joint piece that had the fire seal built in,

The joint was about 4" bigger than the pipework, but didn't intrude internally on it.

We actually scrounged the joints from the HVAC guys as the bloke we were subbing to had no idea what to do.

 
We use the in-duct fire dampers that have internal blades that are under spring tension and held open with a temperature rated link. There's also one that's like a roller shutter door that slams closed, also has a temp rated link but from experience they're more likely to stick. Both types are actually reasonably priced, I think we paid about the equivalent of 50 quid for a 1000x1000 damper not long ago.

Something like this but not sure of a suitable UK supplier.

http://electrovent.co.za/wp-content/uploads/2015/12/Fire-Dampers-EFD.pdf

 