but if manufacturers instructions say it must be fused at something elss than the rating of the shower (highly likely), then it wont comply with the regsYou could comply with the regs and wire straight from the shower in 1.5mm
All your examples are correct but miss the point. We are talking about 2 disporportionally sized cables. How will the smaller be gripped properly? The twist and insulation on a stranded cable will provide an 'ancor' point to stop the cable splaying out but nothing will prevent the smaller cable from ending up not properly secured (and liable to overheat).I don't think a 6A MCB terminal is physically any different from a 40A or 50A MCB terminal yet we all seem able to ensure a correct termination and grip with 1.0mm, 1.5mm, 2.5mm, 6.0mm, 10.0mm conductors. Also the earth and neutral bar terminations all use the same size diameter hole and securing screw. Do you not think that providing any termination is big enough for the largest conductor size required, most competent electricians would be able to ensure their joints are mechanically and electrically sound? I would think the problem to be more the reverse, trying to put too large a cable into a small termination.Doc H.
Terminal capacity, 45A Switches and CCUs:
4 x 4mm2
3 x 6mm2
1 x 16mm2
Terminal capacity, 32A Switch:
3 x 2.5mm2
2 x 4mm2
1 x 6mm2
That to me reads that you can (for example on the 45A switch have 4 up to 4mm cables OR 3 up to 6mm cables OR 1 up to 16mm. cable
---------- Post Auto-Merged at 16:20 ---------- Previous post was made at 16:19 ----------
[quote name='Andy