Hi Justjess , hopefully to help you along .
One thing with faults is ...stop & think & shut out everyone else who may be running about , giving advice , causing confusion. Lights were fine until this morning , so whats happened .
So the old elimination trick is always worth a go . You already did that by finding it is the lighting circuit ...but its tripping the RCD ... NOT the MCB so a short is unlikely .
Theres leakage to earth on the lighting .
1) Is there a faulty fluorescent fitting anywhere ? Might be a ballast or a cable routed past the ballast , melted insulation.
2) Outside light full of water ?
3) Could try turning all the switches OFF and try the RCD ..if it resets ..try switching ON one at a time until it trips again.
4) As said above could disconnect half the circuit and try the RCD , continue to narrow the fault down .
5) Its always a good idea to ask whoever lives there if there was a bang somewhere or a water leak somewhere or some DIY work carried out , owner has changed a light fitting , or has someone messed with the connections in the board ...moved the lighting neutral to the other bar .
Edit : Forgot the one where a squirel / rat / mouse / wombat has chewed the cables .
One thing with faults is ...stop & think & shut out everyone else who may be running about , giving advice , causing confusion. Lights were fine until this morning , so whats happened .
So the old elimination trick is always worth a go . You already did that by finding it is the lighting circuit ...but its tripping the RCD ... NOT the MCB so a short is unlikely .
Theres leakage to earth on the lighting .
1) Is there a faulty fluorescent fitting anywhere ? Might be a ballast or a cable routed past the ballast , melted insulation.
2) Outside light full of water ?
3) Could try turning all the switches OFF and try the RCD ..if it resets ..try switching ON one at a time until it trips again.
4) As said above could disconnect half the circuit and try the RCD , continue to narrow the fault down .
5) Its always a good idea to ask whoever lives there if there was a bang somewhere or a water leak somewhere or some DIY work carried out , owner has changed a light fitting , or has someone messed with the connections in the board ...moved the lighting neutral to the other bar .
Edit : Forgot the one where a squirel / rat / mouse / wombat has chewed the cables .