Martinwigan
Member
Hi guys I attended a call out today to a some alarm fault. It was a mains voltage fire alarm there was a twin coming from consumer unit to 1st smoke head then 3core out to rest of heads. Brown was used for live grey neutral and black was the interlink hence volt free. On testing I had 240v to live n earth and live n neutral. When testing interlink to earth I found 90v and this was causing heads to activate. I traced circuit bk to second point and disconnect out goin leg and fly leads. And tested again and was getting same results. I went to consumer unit and carried out ze and results were megger high so I re terminated all earths n carried out test again and got a good reading of .20 so put this down to bad earth so went and test again and got at second point and got 30volts on the interlink cable even tho the black cable was connected to nothing at any ends. So we put a head back onto the circuit to c if head went of but never and when we tested the voltage again on black cable and it was clear. But I'm still thinking its a bad earth coming into the building. Has anybody come across this befor or anything similar and am I right in thinking it is a bad earth