what if you had two cpc
what if you had two cpc
I have got some steel reducing bushes!Brass is non-ferrous. Can you get ferrous bushes ?
Steps,but the trunking and enclosure are part of the circuit,how do you get the sheath of a SWA into the enclosure when it is used as the CPC?
rubbishthey MUST all go through the same hole
Hi errrm YE...Hi all, Errrm, No.... Scenario 1,
"If you supply the db with two single core swa cables through the same hole, by the fact they are swa, effectively means they have gone through different holes as they will be separated by the swa and eddy currents will be formed in the swa itself"
Single core SWA for an ac circuit is banned outright anyway... [by the same reg]
john..
b:O !!rubbishif you use SWA the cpc doesnt even enter the enclosure, it simply becomes a part of it.
the reg you keep referring to is when the cable/s enter a metal enclosure,
they entered the metal enclosure when they entered the trunking,
but yet the dno are allowed to use concentric cable which effectively creates a single core armoued type cable, although it has the neutral on the outer cores/sheath if pme'd or tncs then the outer sheth part is at earth potential / neutral potential anyway, so therefore no difference in single core armoured.Hi errrm YE...Yes this is what im saying!....THIS IS THE REASON!... you are not allowed to use single core swa, being single core the L & N are both surrounded by bonded armour and therfore have effectively gone through different holes.