Hi Special Location!!Hmm, not sure i understand...I have not got the book in front of me so i am just going by memory here mind!!!!!!
You say that;
"Max Zs does NOT become 1667 with a 30ma RCD.
The max Zs for circuits protected by a 30ma RCD on a TN system must still comply with the values given in Appendix B .."
Without looking at appendix B, i have no idea what it says, but having a guess here, I presume it gives the values of Zs to achieve the appropriate disconnection times in the normal way, I.E. A TN system with ADS catered for by means of an OCPD.
But how does this square with the reg that states that you can use an RCD instead of an OCPD to achieve disconnection times in a TN system [obviously you still have to make provision for overcurrent protection too] which would otherwise be impossible, presumably because of high Zs??
john..