fire alarm sounder

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

dean mac

Member
Joined
Jul 29, 2008
Messages
116
Reaction score
1
Location
england
hi guys my mate who has a pub told me he has a fault on his fire alarm panel i had a quick and noticed someone has unscrewed a sounder on the stairs.

what i would like to know is there anyway of linking the cables out until he finds the sounder many thanks

 
if its 'temporarily' bypassed, i can guarantee it will become permanent. get it fixed. its not that hard to get replacements. most wholesalers will have stuff like that in stock, or a local fire alarm co will have one

 
if its 'temporarily' bypassed, i can guarantee it will become permanent. get it fixed. its not that hard to get replacements. most wholesalers will have stuff like that in stock, or a local fire alarm co will have one
he has the brewrey engineer coming out monday so for now how do u get round it put the 2 reds and blues together on a connector

 
i dont do much with fire alarms, but at a guess, id yes, connect each colour together. there will probably be a EOL which is what the panel will be looking for

 
he has the brewrey engineer coming out monday so for now how do u get round it put the 2 reds and blues together on a connector
If the head is out normally connecting l1 and l2 will enable a bypass.

\this can be done with a temp link.

Or as you say linking both nuetrals and live will give the impresion there is no connection there so bypassing the sounder totally.

Make sure it is never left in this state as any problem and it is seriously fround apon.

 
If the head is out normally connecting l1 and l2 will enable a bypass.\this can be done with a temp link.

Or as you say linking both nuetrals and live will give the impresion there is no connection there so bypassing the sounder totally.

Make sure it is never left in this state as any problem and it is seriously fround apon.
thanks mate

 
Re: fire alarm sounder

Quote:Dean Mac

he has the brewrey engineer coming out monday so for now how do u get round it put the 2 reds and blues together on a connector

21st May 2009 15:20

Sorry a bit late on this one hope it has been replaced and tested.

Confused over the wiring colours Red and Blue 4 core is Brown Blue Grey Black.

must be old Firetuf Red, Black, Blue,Yellow,I would check out with a meter before connecting through as you could naf up the zone wiring and not the sounder circuit.

If in doubt strap it out does not always work.

Normaly red black one pair and yellow blue the other.

Not red Blue, Yellow Black

 
Re: fire alarm sounderQuote:Dean Mac

he has the brewrey engineer coming out monday so for now how do u get round it put the 2 reds and blues together on a connector

21st May 2009 15:20

Sorry a bit late on this one hope it has been replaced and tested.

Confused over the wiring colours Red and Blue 4 core is Brown Blue Grey Black.

must be old Firetuf Red, Black, Blue,Yellow,I would check out with a meter before connecting through as you could naf up the zone wiring and not the sounder circuit.

If in doubt strap it out does not always work.

Normaly red black one pair and yellow blue the other.

Not red Blue, Yellow Black
hi mate in the end i went and got the combined bell smoke and fitted it jobe done
 