To be clear the flickering occurs when the lights are on. Will a snubber work with this as everthing i read about snubbers is to solve flickering when lights are switched off.
Are you not going to answer my questions?
To be clear the flickering occurs when the lights are on. Will a snubber work with this as everthing i read about snubbers is to solve flickering when lights are switched off.
No heavy industry near by.
OkA snubber will work with the lights on, see post 16.
HI
never seen this issue in 35years in the trade and wondered if anybody has any idears.
The property is a new build and the installation fitted by myself. We have 26 Aurora cx7 downlights on 3 seperate circuits and controlled by various switching configurations. All dimmer switches are Varilight V- pro modules and the consumer unit is the new Click Elusian split load board with SPD.
The lights flickers very randomly sometimes not for a day or 2. I have checked everthing. No loose connections. Aurora have sent new fittings which i have fitted. I've changed the dimmer modules but the problem is still there. Has anyone got any idear what this could be or has any body seen this before? I've now hit a wall as to what to do next.
Thanks
Please Note: We do not recommend mixing LED's circuits with products such as extractor fans.This is due to the sensitive nature of LED's and is not product specific.
The snubber shown in post 16 is from RS Components, if I remember had to buy them in a pack of five, the connection is across the feed into the LED, exactly the right width for a Wago lightbox and Wago 294 connector, I only needed to put two into a bank of twelve downlights, but it could depend on the wattage of the LED's.Ok
Will try snubber. Where do i purchase correct one from and where/how on circuit do i connect it? Do i need 1 per circuit or 1 o every bank of lights?
Thanks
I think you need to replace one or two of the Aurora lights with good old fashioned down lights with changeable bulbs and see if that one performs any differently
I’ve seen some odd results where led drivers can affect other lamps on the circuits
Or any filament mains lamp and holder!Been thinking about this and this has to be your next step - just change one of the LED fittings for a GU10 lamp holder and fit a FILAMENT bulb - then if it flickers too you'll know its not LED related
CPC FT00715 is what I have used. One per switched circuit.Ok
Will try snubber. Where do i purchase correct one from and where/how on circuit do i connect it? Do i need 1 per circuit or 1 o every bank of lights?
Thanks
https://electricianforum.co.uk/threads/i-have-found-the-holy-grail.46558/Probably doesn’t add much to the conversation but I’ve experienced this with Bell downlights (integrated units) even when fitted with the Bell dimmer which is supposed to be suited to them I still had a slight flicker and full brightness. Changed from dimmer to switch and flickering went away
I have now remove i of the light circuits from the split load rcd and connected it to BG rcbo and it seems to of sorted the problem?? Any idears why ??HI
never seen this issue in 35years in the trade and wondered if anybody has any idears.
The property is a new build and the installation fitted by myself. We have 26 Aurora cx7 downlights on 3 seperate circuits and controlled by various switching configurations. All dimmer switches are Varilight V- pro modules and the consumer unit is the new Click Elusian split load board with SPD.
The lights flickers very randomly sometimes not for a day or 2. I have checked everthing. No loose connections. Aurora have sent new fittings which i have fitted. I've changed the dimmer modules but the problem is still there. Has anyone got any idear what this could be or has any body seen this before? I've now hit a wall as to what to do next.
Thanks
I have now remove i of the light circuits from the split load rcd and connected it to BG rcbo and it seems to of sorted the problem?? Any idears why ??