Hi,

I went to look at a swimming pool today, the chap wants the heater hooked up to a cu in his shed..

The heater needs a 63a D type mcb and 30ma rcd protection at shed cu. the cable feeding the shed cu is 10mm swa running 20 meters to the house into a 4 way cu containing a 30ma rcd and mcb.

My long winded question is if I was to take the 30ma rcd from house end of cable and swap it for a 100ma rcd, then putting the 30ma in the shed cu, what type/rating of mcb would i need at the house end bearing in mind the heater would be running on a 63a D type mcb?

I know this is basic stuff, but i really am having a 'blonde moment' :Blushing

many thanks

b

 
Don't forget the volt drop as well with a 63A load, so the existing 10mm might not be big enough.

 
Doh! I really am having one of those days....can't see wood for trees.....

bad day explode

 
Volt drop would look ok on 10mm given 63amp as maximum required.

Looks like a drop of 5.64v for 20 meters.

Supply voltage = 230 Volts

Ib - design current = 60 Amps

Protective device type = MCB typeD

In - protective device rating = 63 Amps

Length of run of cable = 20 meters

Power factor = 1

Cable Type : Thermosetting 90

 
Nice one gh. Can you explain the last paragraph for me please as I'd like to understand why that is if you don't mind mate. Is it because zs? ThAnks

 
Yes a type d mcb has a maximum Zs, the calculation I did was for 0.4 sec disconnection which is only applicable to circuits up to 32amp, but I prefer to edge on the side of caution.

A RCD or RCBO reacts to a fault differently to a MCB and can disconnect faster when a typical installtion has a problem with high Zs readings, which is why RCD's are required for installations that are TT.

 
Thanks Mr Hornet,

If i install rcbo at shed cu, what would i install at the house end of the 10mm swa to protect that?

 
Volt drop would look ok on 10mm given 63amp as maximum required.Looks like a drop of 5.64v for 20 meters.

Supply voltage = 230 Volts

Ib - design current = 60 Amps

Protective device type = MCB typeD

In - protective device rating = 63 Amps

Length of run of cable = 20 meters

Power factor = 1

Cable Type : Thermosetting 90
 
Volt drop would look ok on 10mm given 63amp as maximum required.Looks like a drop of 5.64v for 20 meters.

Supply voltage = 230 Volts

Ib - design current = 60 Amps

Protective device type = MCB typeD

In - protective device rating = 63 Amps

Length of run of cable = 20 meters

Power factor = 1

Cable Type : Thermosetting 90
 
Cause it's a heat pump, basically an air conditioning unit running in reverse. The unit itself only needs 6mm conductors but a large type d mcb because of the start up surge (according to manafacturers instructions....) :pray

 