Hi guys, i've also posted this on another forum. sorry!!! but wonder if you could help,
I have been asked to supply power and lighting to a cabin/summerhouse 35 metres from house C.U.
Customer has already installed 7 core 2.5mm SWA underground (he says he "acquired it" from a friend at YEDL)
All calculations are fine for a load max of 2Kw (volt drop approx 5.9v)
My problem is, because it is 7core, the guy wants to include within it, a seperate lighting cct for tree illumination, controlled at the house end when the cabin is isolated.
Just like to know your thoughts regarding safe isolation at house end for anyone in the future working on either circuit, i.e. how you would supply both circuits.
1) from 2 seperate spare ways in c.u. suitably protected
2) create a distribution circuit, either 25mm tails & henley block or 6mm from c.u, to a 2 way "garage" cu and then feed from there within the swa (adaptor box if nescessary)
Also, sorry to be a pain, your thoughts on protection at cabin end.
System is TN-S
No extraneous conductive parts at cabin end
Sorry for long post
Thanx
Mick
I have been asked to supply power and lighting to a cabin/summerhouse 35 metres from house C.U.
Customer has already installed 7 core 2.5mm SWA underground (he says he "acquired it" from a friend at YEDL)
All calculations are fine for a load max of 2Kw (volt drop approx 5.9v)
My problem is, because it is 7core, the guy wants to include within it, a seperate lighting cct for tree illumination, controlled at the house end when the cabin is isolated.
Just like to know your thoughts regarding safe isolation at house end for anyone in the future working on either circuit, i.e. how you would supply both circuits.
1) from 2 seperate spare ways in c.u. suitably protected
2) create a distribution circuit, either 25mm tails & henley block or 6mm from c.u, to a 2 way "garage" cu and then feed from there within the swa (adaptor box if nescessary)
Also, sorry to be a pain, your thoughts on protection at cabin end.
System is TN-S
No extraneous conductive parts at cabin end
Sorry for long post
Thanx
Mick