HI All,
Could do with some help I am replacing an electric ceramic hob with a 7.2kW induction hob.
The existing circuit is wired using 10mm2 and protected by a 32A BS3871 Type 2 circuit breaker.
The existing circuit will then supply a combination of a 5.7kW double oven and the new 7.2kW hob.
Firstly could I run this on the one circuit or would it be better to run on two separate circuits?
Secondly what would be the best cable to connect from the 45A cooker switch or switches to the appliances. I was thinking of using 2.5mm H07RN-F and 4mm H07RN-F