Can you actually see the cable though if you are getting high readings like that I would think there is plastic pipe in the system.Hi BattyI was taught to always test at the pipe as near to clamp as possible, but not on it. The system is fairly dated - client has said that she's going to get a new boiler, so unsure about plastic piping.
I do hope 0.16 is ohms NOT megohms!!! :_| :_|Thanks for all your help guys. Earth clamp was loose and pipe was very green underneath! Scrubbed it so it looked like copper again and fitted new earth clamp. Got a reading of 0.16 megohms. Is this still a bit high? Would changing cable to 10mm make any difference?
Got 0.03 on water.
Its a mansion.I do hope 0.16 is ohms NOT megohms!!! :_| :_|Assuming they are both ohms....
you can check your expected values using the resistance tables in OSG page 166.
so if you are getting reading 0.03ohms for 6mm copper,
then from the table 1m of 6m is 3.08miliohms
(0.03/3.08) x 1000 = 9.7.. suggesting your water bond is round 10m long?
and
0.16ohms of 6mm copper..
(0.16/3.08) x 1000 = 51.9.. suggesting your 'gas?' bond is approx 52m long?
would either of these figures match up with the size of the installation and the likely cable routes? e.g. ups & downs as well as horizontal distances?
IF your one reading IS 0.16MEGohms..
that would give you
(160,000ohm / 3.08) x 1000 = something like 519000 x 100m drums of 6mm!!! :_|
:^O :^O:^O:^O:^O
HTH:x
ROTFWLI do hope 0.16 is ohms NOT megohms!!! :_| :_|Assuming they are both ohms....
That does help - I really need to make better use of my OSG.you can check your expected values using the resistance tables in OSG page 166.so if you are getting reading 0.03ohms for 6mm copper,
and
HTH:x