Hi folks,
Just finishing up a garage conversion into a wood workshop for myself. I’ve trenched in a new 6mm SWA (60 metres in hard clay and rock!), and I’ve wired up all my sockets and lighting circuits on the workshop end, earth rod is in, gland made off garage side, consumer unit all ready for final wiring and wiring on the house side is done.
I’m not an electrician by trade but, I’m about to say it, I have a decent idea of what I’m doing. I’ve wired up plenty 12V, am comfortable enough with 240V and 3-phase to get me close to the finish line, but as I always want things signed off and to be safe, I bring in the sparky for the final wiring.
I’m running all 240V for now, all the usual: planer thicknessers, lathe, chop saw, table saw, extraction system, all the regular power tools etc etc. I figure that at any one time I could be running 4200W lets say; that’s a planer or table saw with the extraction system and a vacuum.
I’ve two 16A radial circuits for the sockets, one side is just chop saw, vacuum and stuff like chargers etc. The other circuit is where the good stuff happens, all the bigger machines.
So here’s where I need some advice. The sparky and his apprentice are not the best.. Messy, slow.. I’ll just say it.. incompetent. All I wanted them to do was make off the gland house side and wire it up, and install the RCBOs or MCBs garage side and wire that up. I figured a guy and his apprentice, 1 day max.
The main guy had to go to Screwfix 3 times as he forgot stuff each time, and took a 2 hour lunch. He did nothing else. The apprentice was left with no tools as they were in the car of the main sparky, so he had to use all of mine, then he proceeded to drill two wrong holes in the cupboard housing the electrical system; one in the wrong place the other too small for the gland that he’d already made off… I had to then drill the correct hole myself. He spent almost 5 hours drilling those wrong holes, making off the gland and then wiring it up. I don’t know enough about wiring up to the consumer unit to check their work and be sure it is all fine, but I’m not left with confidence for the safety of my expensive woodworking machines!
Ranting aside, onto the specs. I originally spec’s Type C RCBO 20A for the machine side, and Type B for the other side. Plus a Type B 6A for the lights. As well as an SPD. They said they couldn’t make the RCBOs work due to age and state of the house side consumer unit - it is a mess in there so fair enough, probably.
I’ve sent them back and replaced them with MCBs instead and an RCD which will go garage side rather than the house. Does this sound correct? And do those specs sound correct for the purpose?
- Type C 20A MCB for machines socket circuit
- Type B 20A MCB for other socket circuit
- Type B 6A for the lights (I’m not fussed about this)
I’m mostly looking for confirmation on the Type C, as I’ve only ever been in workshops with existing power, where I may have added a circuit but I’ve never done all of this from scratch.
If it helps, here’s what I’m running:
Thanks for taking the time folks, it is much appreciated. My safe and cosy machines and fine woodworking will thank you!
Just finishing up a garage conversion into a wood workshop for myself. I’ve trenched in a new 6mm SWA (60 metres in hard clay and rock!), and I’ve wired up all my sockets and lighting circuits on the workshop end, earth rod is in, gland made off garage side, consumer unit all ready for final wiring and wiring on the house side is done.
I’m not an electrician by trade but, I’m about to say it, I have a decent idea of what I’m doing. I’ve wired up plenty 12V, am comfortable enough with 240V and 3-phase to get me close to the finish line, but as I always want things signed off and to be safe, I bring in the sparky for the final wiring.
I’m running all 240V for now, all the usual: planer thicknessers, lathe, chop saw, table saw, extraction system, all the regular power tools etc etc. I figure that at any one time I could be running 4200W lets say; that’s a planer or table saw with the extraction system and a vacuum.
I’ve two 16A radial circuits for the sockets, one side is just chop saw, vacuum and stuff like chargers etc. The other circuit is where the good stuff happens, all the bigger machines.
So here’s where I need some advice. The sparky and his apprentice are not the best.. Messy, slow.. I’ll just say it.. incompetent. All I wanted them to do was make off the gland house side and wire it up, and install the RCBOs or MCBs garage side and wire that up. I figured a guy and his apprentice, 1 day max.
The main guy had to go to Screwfix 3 times as he forgot stuff each time, and took a 2 hour lunch. He did nothing else. The apprentice was left with no tools as they were in the car of the main sparky, so he had to use all of mine, then he proceeded to drill two wrong holes in the cupboard housing the electrical system; one in the wrong place the other too small for the gland that he’d already made off… I had to then drill the correct hole myself. He spent almost 5 hours drilling those wrong holes, making off the gland and then wiring it up. I don’t know enough about wiring up to the consumer unit to check their work and be sure it is all fine, but I’m not left with confidence for the safety of my expensive woodworking machines!
Ranting aside, onto the specs. I originally spec’s Type C RCBO 20A for the machine side, and Type B for the other side. Plus a Type B 6A for the lights. As well as an SPD. They said they couldn’t make the RCBOs work due to age and state of the house side consumer unit - it is a mess in there so fair enough, probably.
I’ve sent them back and replaced them with MCBs instead and an RCD which will go garage side rather than the house. Does this sound correct? And do those specs sound correct for the purpose?
- Type C 20A MCB for machines socket circuit
- Type B 20A MCB for other socket circuit
- Type B 6A for the lights (I’m not fussed about this)
I’m mostly looking for confirmation on the Type C, as I’ve only ever been in workshops with existing power, where I may have added a circuit but I’ve never done all of this from scratch.
If it helps, here’s what I’m running:
- Table Saw 2100W
- Beam Saw 2000W
- Surface Planer 1800W
- Thicknesser 1650W
- Router Table 1500W
- Chop saw 1200W
- Dust collector 1100W
- Extraction 1000W
- Pillar drill 550W
Thanks for taking the time folks, it is much appreciated. My safe and cosy machines and fine woodworking will thank you!