A alworth26 Member Joined Sep 28, 2009 Messages 63 Reaction score 0 Sep 10, 2010 #1 im just wondering what the trip time on a 30ma rcd with a tt system i think its 0.2 and on a tn system 0.4, does any body no wat the correct times are thank you.
im just wondering what the trip time on a 30ma rcd with a tt system i think its 0.2 and on a tn system 0.4, does any body no wat the correct times are thank you.
SPECIAL LOCATION Trailer Boy - Electrician. Supporting Member Joined Mar 28, 2008 Messages 14,458 Reaction score 1,132 Sep 11, 2010 #2 Chapter 11 On site guide. start at page 91 thro page 93.. "Operation of RCD's" or maybe 411.5 TT systems under Additional protection.. maybe even just read the of whole of Ch 41 starts at page 44 of BS7671... should answer most points! :Salute
Chapter 11 On site guide. start at page 91 thro page 93.. "Operation of RCD's" or maybe 411.5 TT systems under Additional protection.. maybe even just read the of whole of Ch 41 starts at page 44 of BS7671... should answer most points! :Salute
tom1 Distinguished Member Joined Aug 7, 2009 Messages 2,331 Reaction score 0 Sep 11, 2010 #3 rcd trip time are the same on tt and tn rcd bs en 4293 200 ms X 1 40 ms X 5 rcd bs en 61009 300 ms x 1 40 ms x 5
rcd trip time are the same on tt and tn rcd bs en 4293 200 ms X 1 40 ms X 5 rcd bs en 61009 300 ms x 1 40 ms x 5
Andy™ ©Resident Geordie™ Supporting Member Joined Jan 1, 2009 Messages 30,662 Reaction score 1,376 Location S. Tyneside Sep 12, 2010 #4 its disconection times that are lower for TT, not RCD trip times
A alworth26 Member Joined Sep 28, 2009 Messages 63 Reaction score 0 Sep 13, 2010 #5 we got told in collage under the 17th eddition 0.2 tt 0.4 tn systems
sparkytim Well-known member Joined Mar 14, 2010 Messages 1,809 Reaction score 1 Sep 13, 2010 #6 They are the MAXIMUM disconnection times, not RCD test times.
A alworth26 Member Joined Sep 28, 2009 Messages 63 Reaction score 0 Sep 13, 2010 #7 ok thanks so if some one asks you wats the disconnection time on a ring main what would it be
sparkytim Well-known member Joined Mar 14, 2010 Messages 1,809 Reaction score 1 Sep 13, 2010 #8 As you correctly posted before, TN 0.4 Sec (400 m S) TT 0.2 Sec (200 m S)
A a1spark Senior Member Joined Jan 24, 2009 Messages 630 Reaction score 0 Sep 13, 2010 #10 In agreement with Sparkytim & andy, and adding... ...for Final circuits up to 32A. and with different times for Non -final circuits [distribution ] ...and just to confuse the issue a bit more......changes planned for Ammendment 1.
In agreement with Sparkytim & andy, and adding... ...for Final circuits up to 32A. and with different times for Non -final circuits [distribution ] ...and just to confuse the issue a bit more......changes planned for Ammendment 1.