I'm currently doing a eicr on a house. It's a Tncs ( PME sticker ) supply, protected by a 100A 1361 (33KA) main service fuse.
I did a ze test at the consumer unit, all parallel paths disconnected, and it came back at 0.01 ... I know its Very low
I then carried out a pfc which came back at 13.5KA
Now the breakers are only rated at 6KA, so my question is, other than write it down on my sheet, what course of action should be recommended ?
Got it never mind, the bs1361 provides the protection, even to the upstream devices, so it complies