Hi I'm in the process of installing a small bd in a out house it has a exsiting 2.5 3 core swa supply of a 16A mcb which I would like to utilise I have calculated the Vd for the swa and it's 6.08v I want to run 2 sockets and 3 florescent lights by using a small DB with a 16A mcb for sockets and a 6A fir lighting both protected by a rcd main switch the problem is after I calculated the volt drop for the lights it goes overthe 3% as you calculate it against the size of mcb not the demand.
If I was to use a 2a mcb volt drop goes just under 3% so all is good in the world again.
Can any one see a problem with this.
Also I should say that the out building has a large steel lintel which will need to be bonded so installation will have to be a tt
If I was to use a 2a mcb volt drop goes just under 3% so all is good in the world again.
Can any one see a problem with this.
Also I should say that the out building has a large steel lintel which will need to be bonded so installation will have to be a tt