Hello.
I have recently attended the Electrical Domestic Installers course and have my 17th Edition. I have good knowledge of Rewires and the domestic area.
today using my fluke 1562 MFT I recorded my Zs value on my house ring main.
between L-N I get what I would expect to get on sockets ... 0.45 ohms. however, when I test between L and PE which is obviously what the Zs test is I get a reading of 560 ohms. yes that it right.
Any ideas what's causing this issue? I have a TNCS supply.
cheers
please say I can take it buddy
I will try to explain it like this, to be a semi reasonable electrician You need a basic understanding of:-
- How to design a circuit for the load(s) it has to supply (including all relevant calculations)
- How to select correct cable capacities taking into account installation environment, external influences, length, volt drop etc..
- How to select correct protective devices for the cable(s) used.
- How to use appropriate methods and materials to install the circuit you have designed.
- The different suppliers earthing arrangements and how they affect the above design/installation aspects.
- Know what dead tests need to be done and what expected results should be.
- Know what dead test equipment should be used and how to use it.
- Know what live tests need to be done and what expected results should be.
- Know what live test equipment should be used and how to use it.
- Knowledge of current statutory and non-statutory regulations and guidance applicable to your alteration / addition, (and/or where to find that guidance to reference any areas that are not immediately familiar).
- Know what paperwork needs to be issued and how to correctly complete all aspects of that paperwork.
- A underpinning knowledge of Maths, Physics, Electrical science and how to evaluate unexpected meter readings to logically interpret and isolate any hazards, dangers or fault symptoms on a circuit.
- Previous wiring regulations and how circuits designed to earlier standards may be electrically safe whilst not appearing to comply with current wiring regulations.
- The ability to evaluate inspect and test older installations, installed by others so as to establish if it is safe to extend or modify an existing circuit.
- The ability to evaluate inspect and test older installations, installed by others to diagnose and rectify fault symptoms when an installation fails to operate how it was originally design to operate.
- Health and safety aspect of your work that can affect your, your customers, any third parties all at the location you are working at.
- etc... etc.. etc..
(the older you are the more experience you gain and understanding in all aspects of the work increases...
BUT you must start with the basics in all areas IMHO)
The bit in red is what most people get from doing a short "17 edition" or "Part-P" electrical couse...
They have are taught a limited knowledge of some wiring regulations so as to pass an exam...
The other 90%+ skills and knowledge needed to work safely and efficiently within the electrical industry are NOT taught on these short courses!!
You have a basic fault finding exercise to do...
the only tips I will say are:-
If in doubt.. go back kill the power.. do the dead tests first....
Prove exactly what you have or haven't got
DO NOT ASSUME ANYTHING!!
Any "apparent faulty reading" has one of three possible causes...
1/ A physical fault or problem on the installation.
2/ A technical fault or problem with the test equipment or its test leads.
3/ A knowledge fault or problem when the person undertaking the testing doesn't understand the test equipment / the readings / or what the installation readings should be.
A logical approach to evaluation and elimination should soon show you where any problem lies.