Hi all, just completed a PIR on a domestic install. The Zs on the RFC is a bit high for a B32 MCB, i'm getting several readings between & around 1.16 ohms (some just below and a few higher), up to the worst being 1.43 ohms. The cct is RCD protected with 30mA protection. The readings were taken with the circuit energised. Also, my reading of the end to end readings of the RFC gave a higher than calculated value for the cpc - could this be the reason for my high Zs maybe? I'm going to give a CODE 3 to investigate the high cpc value further. I seem to remember reading that Zs figures can be higher when taken live, should i repeat the Zs as a dead test? Cheers.