Hi folks just a quick question..
I have a new kitchen coming in and the hob total output is 6.7 kw.
The double oven total output is 4.2 kw.
Will the existing 6mm cable on a 32amp Mcb from the fuse board be enough. The board is very close to the cooker switch it’s only a 10metre run.
It wouldn’t be handy to get another 6mm cable to feed the oven seperately but if it needs done.
First just to confirm some of the math's stuff... Power(Watts)=Volts x Current(Amps)
so Current(Amps) = Power(Watts) / Voltage..
or in your case.. where 6.7kw is 6700watts and 4.2kw is 4200watts... Grand total of 10.9kw (10900watts)
So 10900watts / voltage = current..
BUT.. you would need to double check what voltage the manufactures spec is referencing to...?
As some manufactures, (especially with electric showers), quote power ratings ref 240v..
Not the 230v nominal values used by BS7671` wiring regs..
e.g.
10900w / 230v = 47.39amps
or
10900w / 240v = 45.41amps
This is ASSUMING EVERYTHING could be turned on simultaneously!
Which is where the Diversity calculation mentioned earlier comes in..
BUT diversity is NOT a fixed set of 'one-size-fits-all' rules..
It is guidance to be used by a competent person familiar with the specific installation requirements and expected usage..
And it is possible that actual level of diversity may be higher, lower or not applicable at all!
Also a thing called the installation method will affect how much current a specific cable can safely carry, without potential heat damage..
Dependant upon installation method a 6.0mm CSA T&E cable can be good for 45amps +/- a few percent tollerance..
And I know of several 10.5kwatt showers running happily off a 6.0mm cable via a 45a MCB..
Which would suggest your Oven/Hob arrangement would not be a problem on a 6.0mm cable, but may need a larger MCB?
HOWEVER!............
If you are investing your hard earned time and money into a new kitchen...
I think its generally best to also invest a bit into any possible electrical upgrades improvement's at the same time..
(while an extra supply may not be essential, it could be very beneficial.)
If its just an appliance that's been replaced then you often have to make do with what supply is already in place and work around that!
So to summarise my evaluation..
The existing supply may be OK..
But adding a second supply would be my personal preference unless costa are really astronomically prohibitive!
It could be worthwhile getting an electrician round to asses exactly what's feasible and the costs..
hope that helps?