Hi Guys
I have a customer that is having constant random tripping of their RCD. After quite a lot of investigation I have found two things.
1) There is a lighting track in the kitchen that has LED gu10 style fittings that glow slightly even when the light is switched off. It is a track system and having checked there is a voltage of 34v between earth and neutral.
2) If the hob is connected (not switched on or under load) and I run a loop test on the house main circuit the RCD trips. If I turn off the breaker for the hob the loop test comes back fine. 0.51. I know this is a little naughty but I turned the hob circuit back on and removed the earth for the circuit at the board. The loop test worked fine and showed @ 0.51. As soon as I connected the earth again and ran the loop test it tripped again. I carried out a IR on the circuit from the boards and got 138 ohms. I removed the hob completely and did an IR on the hob and got >299. So I ran another new cable from the board to the hob and did and IR with the hob connected and got 138ohms.
I have no idea what is going on now unless there is a problem with the hob. Do you think the randomness of number 1 could have anything to do with it ?
Any help or pointers would be appreciated
It's a 12way board protected with a RCD MainSwitch 30mA. TNS using suppliers outer sheath for earth. Ze 0.28
Adam
I have a customer that is having constant random tripping of their RCD. After quite a lot of investigation I have found two things.
1) There is a lighting track in the kitchen that has LED gu10 style fittings that glow slightly even when the light is switched off. It is a track system and having checked there is a voltage of 34v between earth and neutral.
2) If the hob is connected (not switched on or under load) and I run a loop test on the house main circuit the RCD trips. If I turn off the breaker for the hob the loop test comes back fine. 0.51. I know this is a little naughty but I turned the hob circuit back on and removed the earth for the circuit at the board. The loop test worked fine and showed @ 0.51. As soon as I connected the earth again and ran the loop test it tripped again. I carried out a IR on the circuit from the boards and got 138 ohms. I removed the hob completely and did an IR on the hob and got >299. So I ran another new cable from the board to the hob and did and IR with the hob connected and got 138ohms.
I have no idea what is going on now unless there is a problem with the hob. Do you think the randomness of number 1 could have anything to do with it ?
Any help or pointers would be appreciated
It's a 12way board protected with a RCD MainSwitch 30mA. TNS using suppliers outer sheath for earth. Ze 0.28