Evening all.
I was wondering whether anybody has experienced any problems with Horstman HRT3 room thermostats?
I have had various call outs to a school where a load of these have been fitted to control 1kw panel heaters. The maximum switching capacity is stated as 10A.
Basically I was called there as one of the stats had started crackling. They isolated the Fused spur. When I arrived I removed the stat and found that the insides where burnt out. Originaly I thaught a loose connection must have caused this.
Anyway since then, another 3 have gone. exactly the same problem.
I had another call today where I had used these to control 300W heat lamps. Was told that one of the stats had started crackling, so they have disconnected the lamp. I am going there tomorrow to replace all the stats.
Has anybody else experienced any problems with these or other stats?
Picture below is what I discovered.
Cheers
GS
I was wondering whether anybody has experienced any problems with Horstman HRT3 room thermostats?
I have had various call outs to a school where a load of these have been fitted to control 1kw panel heaters. The maximum switching capacity is stated as 10A.
Basically I was called there as one of the stats had started crackling. They isolated the Fused spur. When I arrived I removed the stat and found that the insides where burnt out. Originaly I thaught a loose connection must have caused this.
Anyway since then, another 3 have gone. exactly the same problem.
I had another call today where I had used these to control 300W heat lamps. Was told that one of the stats had started crackling, so they have disconnected the lamp. I am going there tomorrow to replace all the stats.
Has anybody else experienced any problems with these or other stats?
Picture below is what I discovered.
Cheers
GS