Just been to price up for some new kitchen lighting. I knew in advance that there was no cpc on the lighting circuit.
Had a quick look at the board, recently done 17th board, all nicely labelled and warning of no cpc on lighting circuit. Looked inside, found the cable, twin sheathed no earth.
Had a look at his EIC, all properly filled in etc except for the lighting circuit.
r1r2 - no entry (expected)
Insulation L to N - >200M
Insulation L to E - >200M (well it would be if there was no earth )
Zs - 0.63 ???? :| ?:| ? :| Where did he take that from, then?